>>>> > We are installing UPS powerchute client on hypervisors.
>>>> >
>>>> > What is the default vms behaviour of running vms when an
hypervisor
is
>>>> > ordered to shutdown: do the vms live migrate or do they shutdown
>>>> > properly (even the restart on an other host because of HA) ?
>>>>
>>>> In general VMs are not restarted after an unexpected shutdown, but HA
VMs
>>>> are restarted after failures.
>>>>
>>>> If the HA VM has a lease, it can restart safely on another host
regardless of
>>>> the original host status. If the HA VM does not have a lease, the
system must
>>>> wait until the original host is up again to check if the VM is still
>>>> running on this
>>>> host.
>>>>
>>>> Arik can add more details on this.
>>>
>>>
>>> I think the question is not related to what happens after the host is
back.
>>> I think the question is what happens when the host goes down.
>>> To me, the right way to shutdown a host is putting it first to
maintenance (VM evacuate to other hosts) and then shutdown.
>>
>>
>> Right, but the we don't have integration with the UPS, so engine cannot
put the host
>> to maintenance when the host lose power and the UPS will shut it down
after
>> few minutes.
>
>
> This is outside of the scope of oVirt team:
>
> Perhaps one could combine multiple applications ( NUT + Ansible +
Nagios/Zabbix ) to notify the oVirt engine to switch a host to maintenance?
>
> NUT[0] could be configured to alert a monitoring system ( like Nagios or
Zabbix) to trigger an Ansible playbook [1][2] to put the host in
maintenance mode, and the trigger should happen before the UPS battery is
depleted (you'll have to account for the time it takes to live migrate VMs).
I would trigger this once power is lost. You never know how much time
migration will take, so best migrate all vms immediately.
It would be nice to integrate this with engine, but we can start by
something
like you describe, that will use engine API/SDK to prepare the hosts for
graceful shutdown.
we already have a role for immediate shutdown of the whole datacenter:
https://github.com/oVirt/ovirt-ansible-shutdown-env
now integrated in ansible collection
https://github.com/oVirt/ovirt-ansible-collection/tree/master/roles/shutd...
--